You still have too much flow restriction on the supply side. Here's a simple test. Disconnect the supply duct off the unit and get a short length of flexible duct to run the supply out through the return grate. And run the AC to see if you have enough flow. Ultimately you may need to add another supply duct out the front of the pedestal of your bed.
The amount of condensate sitting in your drip pan bothers me. I shimmed my units so the side away from the drain dosen't have standing water.