ancora
Guru
- Joined
- Dec 16, 2007
- Messages
- 4,042
The gen set starts right up but only runs about one minute before shutting down. Before shutting down the RPMs drop off. Put jumpers on all the two NC shut down alarms, i.e., exhaust, water temp. and pulled the leads on the NO oil pressure alarm. Replaced the K2 run relay, and the fuel shut-off solenoid, to no avail. Removed mixing elbow..all clear. There is exhaust water flow. The engine mounted 20 amp breaker trips every time the engine shuts down. With only 410 hours on the unit I am perplexed on what to do next.