sndog

Senior Member
Joined
Nov 15, 2022
Messages
244
I am looking at building and installing a fuel polishing system for my boat. My main tank is around 2700 gallons and my other main tank is around 800 gallons. Both can fill, what is called my day tank, which is about 300 gallons. I am wondering if I need to use 1, or 2, racor 1000 filters for fuel polishing system.

Thank you
 
I am looking at building and installing a fuel polishing system for my boat. My main tank is around 2700 gallons and my other main tank is around 800 gallons. Both can fill, what is called my day tank, which is about 300 gallons. I am wondering if I need to use 1, or 2, racor 1000 filters for fuel polishing system.

Thank you
There's no perfect answer. I have two for redundancy, and also to allow polishing at 10 microns and transferring to the day tank thru a 2 micron which matches the filtration of the CAT OEM filter. The other issue is the pump motors. There's no point in having two 1000s if the pump only puts out 3gpm, which is the limit of the Racor. I have two pumps - 1/3 HP ac motors spinning 180 gph carbonator pumps, so can push 6 gpm if both are engaged. The final consideration is what plan B would be if a single pump craps out. In my case, getting fuel to the day tank without the pumps would be very tough, so redundant pumps makes sense for me.
 
There's no perfect answer. I have two for redundancy, and also to allow polishing at 10 microns and transferring to the day tank thru a 2 micron which matches the filtration of the CAT OEM filter. The other issue is the pump motors. There's no point in having two 1000s if the pump only puts out 3gpm, which is the limit of the Racor. I have two pumps - 1/3 HP ac motors spinning 180 gph carbonator pumps, so can push 6 gpm if both are engaged. The final consideration is what plan B would be if a single pump craps out. In my case, getting fuel to the day tank without the pumps would be very tough, so redundant pumps makes sense for me.
Thank you for input. The pump will be used for polishing only. There is another pump, same as the polisher used to transfer fuel between the tanks, and that has its own filter as well. Both pumps are fill-rite 15gpm.
 
My tankage is similar to yours. I tapped into my transfer manifold for the input to the polisher and added a return line to the top of each tank (5). I added a voltage regulator to the system shown to slow down the flow rate. I run through both filters-30 micron then 10 micron. I have long runs (up to 100 feet both ways) through 3/4 inch fuel line, so vacuum gauge is in the red but I have reference points. The only issue I had was blowing up procon pumps. I tried two different procon pumps but both failed. The below pump has worked perfectly for the past year. I used Marine Tex for most of the fittings and haven’t had a single leak. Good luck with your system. Picture below shows Procon pump which was replaced.
 

Attachments

  • IMG_6304.png
    IMG_6304.png
    141 KB · Views: 39
  • IMG_3472.jpeg
    IMG_3472.jpeg
    166.1 KB · Views: 34
My tankage is similar to yours. I tapped into my transfer manifold for the input to the polisher and added a return line to the top of each tank (5). I added a voltage regulator to the system shown to slow down the flow rate. I run through both filters-30 micron then 10 micron. I have long runs (up to 100 feet both ways) through 3/4 inch fuel line, so vacuum gauge is in the red but I have reference points. The only issue I had was blowing up procon pumps. I tried two different procon pumps but both failed. The below pump has worked perfectly for the past year. I used Marine Tex for most of the fittings and haven’t had a single leak. Good luck with your system. Picture below shows Procon pump which was replaced.
Great information. Thank you. Any thoughts in the fill rite pumps?
 
The dayton pump I referenced has sprocket type gears that are connected that give it the torque needed to drive the fluid long distances under pressure. Not sure of your hose diameter or distances and Im not familiar with the fill rite pumps. All that I know is that the Procon pumps designed for high pressure failed twice. Totally different design inside than the dayton rotary gear pump (I rebuilt a used dayton pump).
 
My tankage is similar to yours. I tapped into my transfer manifold for the input to the polisher and added a return line to the top of each tank (5). I added a voltage regulator to the system shown to slow down the flow rate. I run through both filters-30 micron then 10 micron. I have long runs (up to 100 feet both ways) through 3/4 inch fuel line, so vacuum gauge is in the red but I have reference points. The only issue I had was blowing up procon pumps. I tried two different procon pumps but both failed. The below pump has worked perfectly for the past year. I used Marine Tex for most of the fittings and haven’t had a single leak. Good luck with your system. Picture below shows Procon pump which was replaced.
Curious what the specific issue was with the Procon pumps. I have 17 years on mine with no problems.
 
Curious what the specific issue was with the Procon pumps. I have 17 years on mine with no problems.
They worked a little while then seized up like a car engine. Bearing was shot. I feel like it was working to hard to push the distances I needed and then have the added resistance of the two racors. I tried two separate racor models designed for high pressure. I was expecting to much from these pumps.
 
To answer your original question, I would and did use one Racor 1000 filter separator. Below is a picture of my setup. A Racor 1000 is rated for 180 GPH.

What I would do differently next time would be 2 pumps. In essence, you want a fast pump for fuel transfer (3 GPM) and a slower (50 GPH) (bullet proof) pump to run continuously whenever the engine is running or you need to clean suspect fuel.

My choice for the second pump would be a plunger style, most likely Facet / Purolator. Basically they're a magnet coil pulling a plunger up against a spring with 2 simple check valves. They are incredibly reliable, often used in sub 12KW generators, and light sport aircraft. Part of the appeal of plunger style pump is simplicity and a failure of the mechanism can't cause a leak.

Regarding Procon pumps:
The below picture includes a Procon pump. That is my second one. The first one was covered under warranty by WW Grainger. The pump locked up and damaged the motor.



Ted
 

Attachments

  • 20240311_154604.jpg
    20240311_154604.jpg
    133.1 KB · Views: 22
To answer your original question, I would and did use one Racor 1000 filter separator. Below is a picture of my setup. A Racor 1000 is rated for 180 GPH.

What I would do differently next time would be 2 pumps. In essence, you want a fast pump for fuel transfer (3 GPM) and a slower (50 GPH) (bullet proof) pump to run continuously whenever the engine is running or you need to clean suspect fuel.

My choice for the second pump would be a plunger style, most likely Facet / Purolator. Basically they're a magnet coil pulling a plunger up against a spring with 2 simple check valves. They are incredibly reliable, often used in sub 12KW generators, and light sport aircraft. Part of the appeal of plunger style pump is simplicity and a failure of the mechanism can't cause a leak.

Regarding Procon pumps:
The below picture includes a Procon pump. That is my second one. The first one was covered under warranty by WW Grainger. The pump locked up and damaged the motor.



Ted
Totally agree with the two pumps. I should have mentioned I have an independent reverso fuel pump as a transfer pump through a separate filter. I actually used the reverso pump to prime the fuel polishing pump on initial startup.
 